Signs and causes
- Blower runs, air is cold: igniter not glowing, dirty flame sensor, gas valve not opening.
- Lights, then shuts off after seconds: flame sensor coated, or a pressure switch fault from a blocked vent or drain.
- Short cycling: a clogged filter overheats the heat exchanger and trips the limit switch.
- Nothing happens: thermostat, tripped breaker, furnace switch off, door safety switch or a blown control fuse.
- Water around a high-efficiency furnace: blocked condensate drain or a frozen drain line.
Altitude and winter
Gas furnaces in the Pikes Peak region are set up for altitude, because the thin air changes how the burner mixes gas and oxygen. A furnace moved from a lower elevation or installed without adjustment can run rich, produce soot or trip safety switches. High-efficiency furnaces vent through plastic pipes on a side wall; drifting snow can block them, and the furnace will then shut down to protect itself. Clear the pipes outside before calling.
What the technician does
The technician reads any blinking code, checks the filter, igniter, flame sensor, pressure switches, gas pressure and the exhaust, and tests for carbon monoxide. Igniters, flame sensors, pressure switches, inducer motors and control boards are common repairs. A cracked heat exchanger is a safety issue; on an older furnace the technician should explain whether replacement is better value.
Common questions
Why does my furnace blow cold air?
Most often the burner is not lighting or not staying lit, because of a failed igniter, a dirty flame sensor or a blocked vent. A very dirty filter can also overheat the furnace and shut the burners off. Check that the thermostat fan is set to auto, not on, and count any blinking code. Our furnace blowing cold air guide lists the safe checks.
How often should I change the furnace filter?
Check it monthly in winter. Many 1-inch filters need changing every one to three months, and the dry, dusty Front Range air, pets and long heating runs shorten that. Hold the filter up to a light: if you cannot see through it, replace it. A clogged filter makes the furnace overheat and trip the limit switch, which is a common reason for short cycling.
Is a carbon monoxide alarm needed?
Yes. Colorado law requires carbon monoxide alarms near sleeping areas in homes with fuel-burning appliances such as gas furnaces, boilers and water heaters. Test them regularly and replace them when they reach the end of their life. If an alarm sounds, do not try any checks on the furnace. Leave the house and call 911 or your gas utility from outside, then book a technician.
Where this service is available
Colorado Springs · Fountain · Monument
Related guide: Furnace blowing cold air: what to check
Other repairs: Air conditioning repair · Heat pump and mini-split repair · Thermostat, ductwork and airflow